Electricians - Electrical Install Question

I am planning to install a 15A outdoor outlet 30 ft away from the garage.

Yesterday I finished boring under the concrete pathway and installed a PVC pipe to route the cable underneath.

My first question is, what is the minimum code depth for direct burying my 14 awg UF-B cable in Vancouver, WA. I see conflicting info on the web, and looking up the code from the state/county seems impossible.

This site says I only need to bury the cable 12" deep. Other sources say I need to bury 24", and even up to 30".

I'm planning to piggyback this outdoor circuit off of an interior outlet, directly opposite of the interior junction box. I haven't installed this interior outlet yet. Is it acceptable to piggyback outlets on a circuit that is currently only used for garage lighting? I think I will run a new breaker for this new run, since the extra distance isn't too far, but I'm just curious what my other options are. Should I instead put the 2 new outlets on the same circuit that currently handles the existing 3 garage electrical outlets?

I understand that the circuit will require a GFCI prior to exiting the structure, so I will make the new interior outlet be GFCI.

Finally, I would like to run a water line through the same PVC conduit that goes under the concrete pathway to install a sprinkler system. Does code allow for water and electric to run in the same conduit?

__________________
Gas and Electric Vehicle Cost of Ownership Calculator







Give me absolute safety, or give me death!
  Reply With Quote
Alt Today
Popular topics

Other popular topics in this forum...

   
Old 10-25-2014, 07:05 PM   #2 (permalink)
Master EcoModder
 
Join Date: May 2012
Location: USA
Posts: 2,643
Thanks: 1,502
Thanked 279 Times in 229 Posts
Sounds like the making of a future episode of Homes on Homes.

More importantly, what will this be powering? It maybe best to put on its own circuit if this is for an EV charging vs just a couple hundred watt block heater or Christmas lights.
  Reply With Quote
Old 10-25-2014, 09:56 PM   #3 (permalink)
Human Environmentalist
 
redpoint5's Avatar
 
Join Date: Aug 2010
Location: Oregon
Posts: 12,392

Acura TSX - '06 Acura TSX
90 day: 24.19 mpg (US)

Lafawnda - '01 Honda CBR600 F4i
90 day: 47.32 mpg (US)

Big Yeller - '98 Dodge Ram 2500 base
90 day: 21.82 mpg (US)

Prius Plug-in - '12 Toyota Prius Plug-in
90 day: 57.64 mpg (US)

Mazda CX-5 - '17 Mazda CX-5 Touring
90 day: 26.68 mpg (US)

Chevy ZR-2 - '03 Chevrolet S10 ZR2
90 day: 17.14 mpg (US)
Thanks: 4,189
Thanked 4,378 Times in 3,353 Posts
I meant to mention that the outlet was just going to be used for a 20 watt LED landscape light.
__________________
Gas and Electric Vehicle Cost of Ownership Calculator







Give me absolute safety, or give me death!
  Reply With Quote
Old 10-27-2014, 02:34 AM   #4 (permalink)
Human Environmentalist
 
redpoint5's Avatar
 
Join Date: Aug 2010
Location: Oregon
Posts: 12,392

Acura TSX - '06 Acura TSX
90 day: 24.19 mpg (US)

Lafawnda - '01 Honda CBR600 F4i
90 day: 47.32 mpg (US)

Big Yeller - '98 Dodge Ram 2500 base
90 day: 21.82 mpg (US)

Prius Plug-in - '12 Toyota Prius Plug-in
90 day: 57.64 mpg (US)

Mazda CX-5 - '17 Mazda CX-5 Touring
90 day: 26.68 mpg (US)

Chevy ZR-2 - '03 Chevrolet S10 ZR2
90 day: 17.14 mpg (US)
Thanks: 4,189
Thanked 4,378 Times in 3,353 Posts
Here is a map of my plan.

__________________
Gas and Electric Vehicle Cost of Ownership Calculator







Give me absolute safety, or give me death!
  Reply With Quote
Old 10-27-2014, 07:44 AM   #5 (permalink)
toc
EcoModding Apprentice
 
Join Date: Jan 2011
Location: Australia
Posts: 179

Sonata97 - '97 Hyundai Sonata GL
90 day: 25.96 mpg (US)

Pulsar - '03 Nissan Pulsar ST
Team Nissan
90 day: 36.09 mpg (US)

Lancer - '04 Mitsubishi Lancer
90 day: 31.11 mpg (US)

Lancer 2.0 - '09 Mitsubishi Lancer
90 day: 27.1 mpg (US)
Thanks: 9
Thanked 16 Times in 13 Posts
Quote:
Originally Posted by redpoint5 View Post
, I would like to run a water line through the same PVC conduit that goes under the concrete pathway to install a sprinkler system. Does code allow for water and electric to run in the same conduit?
Water and electricity here would be an absolute no.

Bury 600mm in orange conduit for the full run of cable. Safety first.
__________________

Last edited by toc; 10-27-2014 at 07:47 AM.. Reason: better suggest conduit for cable
  Reply With Quote
The Following User Says Thank You to toc For This Useful Post:
Cobb (10-28-2014)
Old 10-27-2014, 09:45 AM   #6 (permalink)
one of thOOOse people
 
Join Date: Mar 2009
Location: the cloud(s)
Posts: 293

twitchy - '98 honda civic dx + sir + ls
90 day: 30.2 mpg (US)

Norman - '14 Ford E-350 EXT
90 day: 16.18 mpg (US)

Silver - '12 VW Golf Base
90 day: 26.1 mpg (US)

Sparta - '19 Honda CB300R
90 day: 84.07 mpg (US)
Thanks: 0
Thanked 81 Times in 66 Posts
I agree that water should definately not share a conduit with electric ever!
The depth of the trench usually is due to the local frost line. 3+ feet here in MA, but I don't know in OR. There is cable availible that can be buried legally without conduit, but that too could conflict with local code. Keep the cable in conduit all the way down the wall and up to the outlet mounted to the tree at the end. It can be without conduit for the horizontal run if deep enough. You should add a foot of sand on top of the cable.
There should not be any problem adding this new recepticle to the existing two garage outlets. Those in the garage *should* already be GFI protected. If they are not, add your GFI to the first in the chain. Do not however put two GFI recepticles on the same circuit as they tend to cancel eachother out.

Last edited by hamsterpower; 10-27-2014 at 09:52 AM..
  Reply With Quote
Old 10-27-2014, 02:15 PM   #7 (permalink)
Human Environmentalist
 
redpoint5's Avatar
 
Join Date: Aug 2010
Location: Oregon
Posts: 12,392

Acura TSX - '06 Acura TSX
90 day: 24.19 mpg (US)

Lafawnda - '01 Honda CBR600 F4i
90 day: 47.32 mpg (US)

Big Yeller - '98 Dodge Ram 2500 base
90 day: 21.82 mpg (US)

Prius Plug-in - '12 Toyota Prius Plug-in
90 day: 57.64 mpg (US)

Mazda CX-5 - '17 Mazda CX-5 Touring
90 day: 26.68 mpg (US)

Chevy ZR-2 - '03 Chevrolet S10 ZR2
90 day: 17.14 mpg (US)
Thanks: 4,189
Thanked 4,378 Times in 3,353 Posts
I don't understand the purpose of GFCI outlets. The circuit breaker is already protecting from excessive current, so why put a second circuit breaker in?
__________________
Gas and Electric Vehicle Cost of Ownership Calculator







Give me absolute safety, or give me death!
  Reply With Quote
Old 10-27-2014, 03:07 PM   #8 (permalink)
Not Doug
 
Xist's Avatar
 
Join Date: Jun 2012
Location: Show Low, AZ
Posts: 12,186

Chorizo - '00 Honda Civic HX, baby! :D
90 day: 35.35 mpg (US)

Mid-Life Crisis Fighter - '99 Honda Accord LX
90 day: 34.2 mpg (US)

Gramps - '04 Toyota Camry LE
90 day: 35.39 mpg (US)

Don't hit me bro - '05 Toyota Camry LE
90 day: 35.79 mpg (US)
Thanks: 7,217
Thanked 2,217 Times in 1,708 Posts
Quote:
Originally Posted by redpoint5 View Post
I don't understand the purpose of GFCI outlets. The circuit breaker is already protecting from excessive current, so why put a second circuit breaker in?
Breakfast in bed is good. Breakfast in bath is better.
  Reply With Quote
Old 10-27-2014, 10:37 PM   #9 (permalink)
Human Environmentalist
 
redpoint5's Avatar
 
Join Date: Aug 2010
Location: Oregon
Posts: 12,392

Acura TSX - '06 Acura TSX
90 day: 24.19 mpg (US)

Lafawnda - '01 Honda CBR600 F4i
90 day: 47.32 mpg (US)

Big Yeller - '98 Dodge Ram 2500 base
90 day: 21.82 mpg (US)

Prius Plug-in - '12 Toyota Prius Plug-in
90 day: 57.64 mpg (US)

Mazda CX-5 - '17 Mazda CX-5 Touring
90 day: 26.68 mpg (US)

Chevy ZR-2 - '03 Chevrolet S10 ZR2
90 day: 17.14 mpg (US)
Thanks: 4,189
Thanked 4,378 Times in 3,353 Posts
I Googled it.

Quote:
Ground Fault Circuit Interupter device protects us from receiving electric shocks from faults in the electrical devices we use in our home. It works by comparing the input current on the hot side to the output current on the neutral side. If there's the slightest difference in current, on the order of a few milliamps, then there is current leaking out somewhere, possibly through somebody's body. To protect us in this situation, the device very quickly cuts off the power supply to the leaking device, within 20-30 milliseconds, greatly reducing any possible human tissue damage from errant current.
So it doesn't trip to protect against fires from excessive current use, but instead trips if electricity leakage occurs to protect against electrocution.

It seems excessive considering how wimpy our 120v AC is in the States.
__________________
Gas and Electric Vehicle Cost of Ownership Calculator







Give me absolute safety, or give me death!
  Reply With Quote
Old 10-28-2014, 09:27 AM   #10 (permalink)
Rat Racer
 
Fat Charlie's Avatar
 
Join Date: May 2011
Location: Route 16
Posts: 4,150

Al the Third, year four - '13 Honda Fit Base
Team Honda
90 day: 42.9 mpg (US)
Thanks: 1,784
Thanked 1,922 Times in 1,246 Posts
Quote:
Originally Posted by redpoint5 View Post
Here is a map of my plan.

How about plan B? Admittedly no sprinkler line, but less of a lot of other things.


__________________

Quote:
Originally Posted by sheepdog44 View Post
Transmission type Efficiency
Manual neutral engine off.100% @MPG <----- Fun Fact.
Manual 1:1 gear ratio .......98%
CVT belt ............................88%
Automatic .........................86%