Swamp Cooler Theory 102
It's ALL about LOTs of surface area with evaporative coolers. With mister's, yes, there are lots of droplets, but they're tiny and they're w-i-d-e-l-y separated and thus provide surprisingly small amount of surface area.
The aspen excelsior pads are usually 1"-2" thick, with the wood fibers oriented perpendicular to the airflow through them, so the air has to flow OVER / UNDER / THROUGH / BETWEEN lots and lots of wetted wood shaving fibers.
However, the OTHER major player in how well (or not) the evap cooler "works" is: (a) the DEW POINT temperature (Tdp) and (b) it's cohort, WET BULB temperature (Twb).
When the outside dry bulb temperature (Tdb) is above 95ºF and the dewpoint temperature (Tdp) exceeds 50-54ºF (just 22-25%RH!), the wet bulb temperature (Twb) will NOT be lower than 67-69ºF...and although this number LOOKS like really cool air, it is NOT, unfortunately, what you actually GET from the evaporative cooler.
With most evaporative coolers you only achieve about 80%-saturation, so you only "get" 80% of the Wet Dulb Depression temperature (WBD = Tdb - Twb):
T(cooler) ~ Tdb - 0.8*WBD
T(cooler) ~ Tdb - 0.8*(Tdb - Twb)
So, if Tdb is 95ºF and Twb is 67-69ºF, the air blowing from the cooler [ T(cooler) ] will only get down to about 73-74ºF...at almost 80%RH! But, your body wants to see/free something below 72ºF and closer to 30-50%RH!
This is when / why they're called "swap" coolers, because when it's HUMID you feel like you're in a tepid "sweat" sauna in a swamp!