I'm still confused. Both houses have grounds, so all circuits will have proper ground wiring.

The old house essentially becomes a subpanel of the new house at that point. So do sub panels need hot/neutral, AND ground connecting them? If so, why?

Quote:
No, It doesn't matter in the main panel. Yes, it matters in the sub panel. First, REMOVE the bonding strap that connects the two bus bars in the sub-panel. Then in the sub, it should be visually obvious that one of the bus bars is insulated from the case. If not, use a volt meter to find out. The insulated one is for neutral. The one that conducts to the case is ground.
What is the purpose of removing the bonding in the sub, but not in the main panel?

Visuals probably helps explain these questions.