07-18-2019, 12:43 AM
#11 (permalink)
That's such a long run it may be better to have the power company run a service lateral and use a standard residential 37kw pad transformer. But they may have a maximum limit to the length of the underground wire.
I don't think the underground part is limited in length ... but they do have line length limits from the 15KV distribution transformer to the residential pad. I think
If you have 575 volt then you already need a transformer.
We have several transformers - we do our own distribution within the plant site. I don't want to pay for ANOTHER transformer.
A residential over head high voltage to single phase is probably cheaper than an industrial 575 to 240v transformer.
To run 37kw on 4,160v they would only need to run about a 12 gauge feeder wire. So the trench, conduit ect would be small, so less parking lot to fix.
I don't think it would be reasonable to get another SaskPower (utility) feed.
Our local utility distributes residential at 14,400V (they still call it 15KV) and the transformer that they install if you don't ask for anything extra is a 200 amp service at 240 VAC. That's less than one 50 KW fast charger, isn't it?
37 kw at 4160V is still less than one fast charger. I guess I'm a bit confused?
Industrial distribution in Saskatchewan starts at 72 KV, but you are encouraged to install at least 138 KV, and we were encouraged to install 230 KV when we did our last expansion in 2012.
Our site is fed with 230KV and the site covers about 2 miles by a mile. We step the 230KV down to 15KV, and use a separate 15KV building to house our 15KV feeders that distribute to the various buildings. The 575V transformers range from 1000 KVa to 4000 KVa. We also have a few 4160V transformers that range from 2500 KVa to 6000 KVa. But I don't have a 4160V feed closer than a quarter mile. It's just not practical.
It's also a matter of economics and space. We have an existing 15KV distribution building with limited room. Our electrical group is rather protective of the 1 or 2 breakers that we have spare. If we used one, the 15KV distribution breaker, buss, metering, protection, etc are quite expensive. North of $50K per cell. And the 15KV building is a long way from the parking lot - maybe 1200 - 1500 feet.
One of our standard 15KV to 575V transformers (1250 KVA) takes some room, as well as a 15KV disconnect, a distribution panel, etc that would need to be outdoor rated and would end up taking at least 2 of the parking spots. We'd have to put fencing around the 15KV gear as well. So less parking spots, and less money for buying EV chargers. I would have 1250 KVa instead of 350 KVa ... I think that's a lose-lose scenario. Or am I missing something?
My apologies for not posting all of the relevant information for the design up front .. but my issue is that the suppliers, or the charger vendors ... won't tell me how or if their chargers talk to each other to share the available power. Can they accept 575V three phase directly? Do I need a breaker and a disconnect for each of their chargers? Somebody has this info ... somewhere ..
In THEORY there is no difference between Theory and Practice
In PRACTICE there IS!
07-18-2019, 04:47 AM
#12 (permalink)
I didn't think you were installing fast chargers.
DC fast chargers can probably take 575 volt power, but j1772 can't.
07-18-2019, 10:25 AM
#13 (permalink)
From a purchasing view: if they won't talk about being interconnected, then they dont interconnect.
Pick a common local universal standard. Whatever the local places use.
Except for the Tesla and oilpan, nobody NEEDS super quick charging, and everyone I know has a box of adapter plugs. I don't believe someone will show up at work bone dry and then have to drive a hundred klicks by lunch. If they do, it shouldn't be your problem to fix.
I was happy my work allowed me to plug into the 117v school bus prewarmer circuit or the pipe warmer circuit when I was running FLA.
07-18-2019, 01:24 PM
#14 (permalink)
Good point!
J1772 seems to be what is used most. It's just sort of the minimum.
Maybe not this year or next. But in 10 years that could be considered 'normal' ... who is to know?
This is Saskatchewan, Canada. It gets cold here. Like 40 below F, -40C. So we have 10A at 120V available at each parking spot to run the block heaters and interior car warmers that everyone has in their ICE vehicles. That's the good news.
But 10A * 120V .. 1200W gets you about 10 KW-h in an 8 hour shift. Minus whatever power is required to heat up the batteries so that they can take the charge (Lithium packs don't really charge when they are below 0C, so the liquid cooling/warming system needs power to warm up the batteries before/during the charge). That's the bad news. There's power ... enough maybe in spring, summer and fall. Not enough in winter.
Since someone at head office decided that our sites should be greener, and EV charging is becoming a thing ... we got some money to engineer/investigate how to put in charging infrastructure.
Taa-Daa!
I still need information, if anyone has some!
I thought this forum would be a good place to start. I'll be sending out formal info requests to ABB, Eaton, Siemens, and whoever else I can find contact information for when I get back from vacation.
I like having *SOME* information before I send out the info requests. It helps when I know what I'm asking for.
07-18-2019, 04:33 PM
#15 (permalink)
I would go with 30a 220 outlets for employees, and something bigger for the visitor spots, the people above you wanting to say they are going green don't care about how much power each employee can get, they are counting spots.
The Following User Says Thank You to roosterk0031 For This Useful Post:
07-19-2019, 09:26 AM
#16 (permalink)
What he said.
The bus warmer example was for illustrating that I was happy at 1KW.
I've been to Grand Forks AFB, NoDak, I know cold.
07-20-2019, 06:13 AM
#17 (permalink)
As far as I can tell the big industrial suppliers don't mess with car charging stuff.
My home chademo peaks at about 8kw, but averages about 7kw, which is almost no improvement over standard 6.6kw charging found on 2013 and up electric vehicles.
But I do have a 100 amp 240v circuit going out to my garage, it's for my welder. But I could breaker it at 80 amps for continuous use, some kind of 70 amp j1772, but no one makes a 70 amp j1772 charging car yet.