Unsolved Mystery: House Interior Found Covered in Ice

Here's a challenge for any Plumber, HVAC tech, Scientist, Physicist, Forensic Investigator, or anyone here with some kind of idea as to what happened -- I'm racking my brain, can't sleep trying to figure it out, and I'm getting nowhere.

The Scene: a 1930's, 2-bedroom, 2-story house with basement, in Northeastern Ohio. Heating System: hot-water heat and radiators by gravity feeding (no pump is involved), automatic water filling, and what I believe to be an "expansion tank". The residence is occupied sporadically by a close family member. Temperature setting: 55F while away.

The family member returned to the house after a cold snap (sub-zero temps). The whole house was freezing cold, and nearly every surface had a layer of ice on it: walls, windows, doors mirrors, inside closets, and mostly in the basement (icicles where all over the place in this area).

The hot water boiler had failed at some point and clearly vented a large amount of steam into the house. It looks like it started at or near the boiler unit (it was converted from a coal-fired system, to natural gas in the 50's). The water bill reflects a large amount of water used in roughly 2-weeks.

The Mystery: 2 of the 7 cast iron radiators had a chunk blown out of the side...



These things weigh a LOT, and are as strong as they are heavy. You couldn't do that with a sledgehammer.

This is the part that has me stumped. Even the plumber and HVAC guy (an old-timer in the biz) said that they had never seen or heard of anything like it -- both the radiator blow-out, and the steam-to-ice incident.

Investigation: I visited the place tonight. The clean-up crew and sub-contractors had installed a high-efficiency, forced-air (natural gas) burner, and placed a temporary duct into the basement. Future vent holes have been cut in the floor to let the heat rise, and thaw the ice. "Moldy" is an understatement. Even light fixtures in closets were dripping wet. All the carpet had to be removed (it was crunchy with ice when first found).

Theory: The boiler cracked (perhaps the exansion tank) and expelled a large amount of steam and hot water into the basement. As it rose, the steam permeated every room, closet, and the attic. The system compensated by adding more water to the system and kept the steam process going until...

The point at which the boiler failed entirely is a mystery. It's a simple system of "open gravity flow", heat, and water. It completely quit, and froze-up the house.

How did the radiator burst? The weakest point is a small valve to bleed air from the line, at the top of each rad. What blew, was the opposite side, at the top.

Could excessive line pressure do it and force more steam into each of the 2 rooms? Did the water not return after failure and it turned to solid ice, expanded, and ruptured the iron? If the expansion tank fails, the system fills with steam instead of water, does not have adequate return and calls for the feed line to provide fresh water. What prompted the system to quit? Perhaps the steam damaged the thermostat, or the circuit to engage the system. The pilot light could have extinguished, forcing a shut-off of gas via thermocouple

3rd Party Testimony: No solid ice was reported in the radiators. The boiler was dismantled and recycled -- no report on its condition, other than "covered in ice". It had to be removed to install a temporary furnace until the replacement was installed -- to begin the thawing process. The house is nearly thawed, and will be de-humidified, and repaired. In the meantime plumbing and electrical components are being replaced.

I can't seem to get a straight theory out of anyone. All they know is that the boiler cracked (or component), the house was steamed-up, the heating system failed, the condensed steam turned to ice, and the place was wrecked.

Luckily I moved a bulk of antiques and family heirlooms back to KC last summer. That was a task! But it's sad to see the place in such a state. I always remembered it as very well maintained and organized.

So, that's the mystery. The biggest things I'm trying to figure is 1) how the heck did a solid piece of cast iron bust 2) what exactly failed and spewed steam; and 3) at what point did the boiler say, "Enough is enough"?

RH77

__________________
“If we knew what we were doing, it wouldn't be called research” ― Albert Einstein

_
_
  Reply With Quote
Alt Today
Popular topics

Other popular topics in this forum...

   
Old 01-31-2009, 03:26 AM   #2 (permalink)
EcoModding Apprentice
 
Join Date: Jan 2009
Location: Macon,GA
Posts: 176

Ruint Taco - '19 Toyota Tacoma SR Double Cab
90 day: 23.76 mpg (US)
Thanks: 124
Thanked 44 Times in 35 Posts
Wow.
  Reply With Quote
Old 01-31-2009, 09:23 AM   #3 (permalink)
Master EcoModder
 
Join Date: Aug 2008
Location: South Dakota
Posts: 460

WonderWagon - '94 Ford Escort LX
Last 3: 51.52 mpg (US)

DaBluOne - '99 Ford Escort SE
90 day: 48.97 mpg (US)

DaRedOne - '99 Ford Escort ZX2 Hot
Thanks: 0
Thanked 15 Times in 4 Posts
Yeah, Wow!
It's the 2 (2 not 1) radiators burst in the same way that has me most puzzled.
What do the nside faces of the broken off pieces look like?
Any rust marks that would suggest they broke along preexisting stress fractures?
  Reply With Quote
Old 01-31-2009, 10:37 AM   #4 (permalink)
Master EcoModder
 
metroschultz's Avatar
 
Join Date: Dec 2007
Location: Norfolk, Va. USA
Posts: 869

CPT SLO - '93 GEO Metro plainjane
90 day: 53.91 mpg (US)

SilverHairBeauty - '01 Toyota Avalon XL
90 day: 24.06 mpg (US)
Thanks: 14
Thanked 33 Times in 28 Posts
Send a message via AIM to metroschultz
I'm going with;
After the failure, water settled in the radiators,(My mom still has them also) and when everything froze, the water froze as well. Bursting the radiators. Sometime later there was a slight warm up, anything over 33 would be sufficient, and that water melted and ran into the carpets.
That's my story and I'm sticking to it.
S.
__________________


When you are courting a nice girl an hour seems like a second. When you sit on a red-hot cinder a second seems like an hour. That's relativity.
Albert Einstein
  Reply With Quote
Old 01-31-2009, 10:52 AM   #5 (permalink)
Master EcoModder
 
Join Date: Aug 2008
Location: South Dakota
Posts: 460

WonderWagon - '94 Ford Escort LX
Last 3: 51.52 mpg (US)

DaBluOne - '99 Ford Escort SE
90 day: 48.97 mpg (US)

DaRedOne - '99 Ford Escort ZX2 Hot
Thanks: 0
Thanked 15 Times in 4 Posts
metroschultz, that's what I thought at first too.
But he said -
Quote:
How did the radiator burst? The weakest point is a small valve to bleed air from the line, at the top of each rad. What blew, was the opposite side, at the top.
Unless he meant something other than what he wrote, don't think your theory will hold water.
  Reply With Quote
Old 01-31-2009, 10:56 AM   #6 (permalink)
Master EcoModder
 
metroschultz's Avatar
 
Join Date: Dec 2007
Location: Norfolk, Va. USA
Posts: 869

CPT SLO - '93 GEO Metro plainjane
90 day: 53.91 mpg (US)

SilverHairBeauty - '01 Toyota Avalon XL
90 day: 24.06 mpg (US)
Thanks: 14
Thanked 33 Times in 28 Posts
Send a message via AIM to metroschultz
Oh poo
It appears to be at the bottom from the pic.
I even thought I saw (no not a puddy tat) the inlet behind the break.
so much for me thinkin again.
__________________


When you are courting a nice girl an hour seems like a second. When you sit on a red-hot cinder a second seems like an hour. That's relativity.
Albert Einstein
  Reply With Quote
Old 01-31-2009, 01:17 PM   #7 (permalink)
Master EcoModder
 
Join Date: Jun 2008
Location: Earth
Posts: 5,209
Thanks: 225
Thanked 811 Times in 594 Posts
My guess is that there was first a failure of the boiler, so that it didn't come on for a long enough time that the house temperature dropped well below freezing. Water in the radiators froze, and the expansion cracked them. (Were the chunks "blown out" of the radiator right by the radiators, or some distance away?) Then later the boiler came back on, so the steaming hot water ran out the holes and froze on the cold surfaces.
  Reply With Quote
Old 02-01-2009, 12:35 AM   #8 (permalink)
Depends on the Day
 
RH77's Avatar
 
Join Date: Nov 2007
Location: Kansas City Area
Posts: 1,761

Teggy - '98 Acura Integra LS
Sports Cars
90 day: 32.74 mpg (US)

IMA - '10 Honda Insight EX
Team Honda
90 day: 34.76 mpg (US)

Tessie - '06 Acura TSX Base
90 day: 28.2 mpg (US)
Thanks: 31
Thanked 41 Times in 35 Posts
Good responses...

The pic shows the radiator upside-down on the floor -- so the top piece ruptured. The piece didn't appear to become a projectile, but was found a few feet from the rad.

I think that hole shown is on the return side: the water fills the radiator to the top at each fin, flows through the final top passage as it cools, and drops to the bottom to be on its way at the return pipe.

I talked to some more family today. Another theory is that the boiler was in good condition. The supply line froze and didn't provide sufficient water to the system. Meanwhile, the system is heating up with steam and the components become hot. The frozen pipe then thaws and releases a rush of near-freezing water into the hot system and the violence ensues: with a possible rupture in the tank, supplying the steam. Then the system quit, froze-up and provided enough freezing power to bust the iron.

Maybe the insurance adjuster will shed some light into the matter.

It's a puzzling case for sure...

-Rick
__________________
“If we knew what we were doing, it wouldn't be called research” ― Albert Einstein

_
_
  Reply With Quote
Old 02-01-2009, 03:48 PM   #9 (permalink)
EcoModding Apprentice
 
Bicycle Bob's Avatar
 
Join Date: May 2008
Location: N. Saskatchewan, CA
Posts: 1,805

Appliance White - '93 Geo Metro 4-Dr. Auto
Last 3: 42.35 mpg (US)

Stealth RV - '91 Chevy Sprint Base
Thanks: 91
Thanked 460 Times in 328 Posts
Aha! Water in a container freezes from the top down.

So, how about - furnace vents steam into a cold house, but it is not sufficient to prevent freezing of everything, including the rad.
  Reply With Quote
Old 02-01-2009, 06:03 PM   #10 (permalink)
Custom User Title
 
Join Date: Jul 2008
Location: Bozeman, MT
Posts: 248

Daily Driver - '02 Pontiac Grand Prix SE
90 day: 18.45 mpg (US)
Thanks: 1
Thanked 6 Times in 5 Posts
Bob's theory was what I'm thinking. If the ice had no where to expand (no air trapped in the radiators, some old places have that) they as the temps drop, the ice forms, but the water had no where to go, so it forces the ice out the top.

So its all water system? No antifreeze? Antifreeze could have prevent the catastrophic failure. Would have made it a slush, but not frozen.