Run Whole House on Wimpy Generator?
I've been seeing "deals" on "power stations" lately; battery plus inverter combos in one. My natural reaction to "all in one" things is that it limits usefulness by locking you into several parameters, and doesn't allow selectively choosing each component for quality, performance, etc.
This got me to thinking I could build my own "power station" using a 12v pure sine wave inverter and battery of my choosing. Once down that rabbit hole, that got me to thinking I could select an inverter sufficiently powerful to run all 120v circuits in my house. The only 240v things I run are the AC, and the oven (range is gas). So, I could switch off my 240v breakers and the mains in a power outage, and wire an inverter directly into the panel (not recommending anyone do this).
I had impulse bought an 800 watt Sportsman GEN1000i generator for $159. This got me to thinking that since my average household load is 600 watts, I should be able to run off my generator if there was a buffer to handle peak loads.
So, my idea is to run generator > 12v battery charger > 12v battery > inverter > breaker panel.
Does this seem feasible? If so, I could potentially run my whole house on 2 gallons of gas per day on a quiet and efficient generator during outages.
Generator
Battery charger TBD. Dad has a 40 amp charger to test the theory with.
Battery... whatever is laying around
Inverter- torn between the $50 cheaper 2500 watt unit that has an LCD screen
https://www.amazon.com/dp/B0BQ3WYBZL...g_paid-20&th=1
and the 2500 watt more expensive unit that has AC out terminals instead of just outlets.
Anyhow, that's the silly project I've been pondering. The advantage of such a system is it can be portable for camping if I wanted to.
|
|
|
The Following User Says Thank You to redpoint5 For This Useful Post:
|
|
Today
|
|
|
Other popular topics in this forum...
|
|
|
02-04-2023, 08:38 PM
|
#2 (permalink)
|
EcoModding Lurker
Join Date: Dec 2022
Location: Winder GA
Posts: 3
Thanks: 27
Thanked 4 Times in 3 Posts
|
Your 120v circuits are going to be wired to one or the other of the 2 phases of the 240v service entrance voltage.
You will have to take that into consideration and jumper the two 120v together. Not a good thing if you forget to un jumper and go back to grid power.
I think you are going to pop something when trying to hook the inverter and generator power together.
Power line workers have been killed by back fed home generated power that reaches the transformer and then gets 'stepped up' to 12k or so volts on the grid that they know is turned off.
|
|
|
The Following 2 Users Say Thank You to Dodge 1996 4x4 Dan For This Useful Post:
|
|
02-04-2023, 08:44 PM
|
#3 (permalink)
|
Human Environmentalist
Join Date: Aug 2010
Location: Oregon
Posts: 12,754
Thanks: 4,316
Thanked 4,472 Times in 3,437 Posts
|
Quote:
Originally Posted by Dodge 1996 4x4 Dan
Your 120v circuits are going to be wired to one or the other of the 2 phases of the 240v service entrance voltage.
You will have to take that into consideration and jumper the two 120v together. Not a good thing if you forget to un jumper and go back to grid power.
I think you are going to pop something when trying to hook the inverter and generator power together.
|
Welcome to the forum.
One of the inverters I'm considering doesn't have AC power blocks, so if I were to power both legs of my panel with the full output capability, I think I'd need to use 2 outlets and make sure the hot and the neutrals are sorted out properly.
|
|
|
02-04-2023, 10:44 PM
|
#4 (permalink)
|
Corporate imperialist
Join Date: Jul 2011
Location: NewMexico (USA)
Posts: 11,266
Thanks: 273
Thanked 3,569 Times in 2,833 Posts
|
Sounds like you want at least a 24v system.
__________________
1984 chevy suburban, custom made 6.5L diesel turbocharged with a Garrett T76 and Holset HE351VE, 22:1 compression 13psi of intercooled boost.
1989 firebird mostly stock. Aside from the 6-speed manual trans, corvette gen 5 front brakes, 1LE drive shaft, 4th Gen disc brake fbody rear end.
2011 leaf SL, white, portable 240v CHAdeMO, trailer hitch, new batt as of 2014.
|
|
|
02-05-2023, 12:25 AM
|
#5 (permalink)
|
Human Environmentalist
Join Date: Aug 2010
Location: Oregon
Posts: 12,754
Thanks: 4,316
Thanked 4,472 Times in 3,437 Posts
|
Quote:
Originally Posted by oil pan 4
Sounds like you want at least a 24v system.
|
Thought about it, then thought 12v is more versatile. Worst case, I run the inverter and a car to charge the battery.
So you see no fundamental flaws with the concept?
|
|
|
02-05-2023, 01:48 AM
|
#6 (permalink)
|
Corporate imperialist
Join Date: Jul 2011
Location: NewMexico (USA)
Posts: 11,266
Thanks: 273
Thanked 3,569 Times in 2,833 Posts
|
12v is for when you are experiencing to use about 2kwh per day or less. For backup power for a refrigerator and a few small items or camping because of the 12v.
Cars only have about 10 amps available for charging with everything off, idling. Burning a L of gas per hour or more for 10 amps sucks.
A 24v alternator strapped to a 3hp predator engine can do better than that, a lot better.
__________________
1984 chevy suburban, custom made 6.5L diesel turbocharged with a Garrett T76 and Holset HE351VE, 22:1 compression 13psi of intercooled boost.
1989 firebird mostly stock. Aside from the 6-speed manual trans, corvette gen 5 front brakes, 1LE drive shaft, 4th Gen disc brake fbody rear end.
2011 leaf SL, white, portable 240v CHAdeMO, trailer hitch, new batt as of 2014.
|
|
|
02-05-2023, 01:54 AM
|
#7 (permalink)
|
Human Environmentalist
Join Date: Aug 2010
Location: Oregon
Posts: 12,754
Thanks: 4,316
Thanked 4,472 Times in 3,437 Posts
|
Quote:
Originally Posted by oil pan 4
12v is for when you are experiencing to use about 2kwh per day or less. For backup power for a refrigerator and a few small items or camping because of the 12v.
Cars only have about 10 amps available for charging with everything off, idling. Burning a L of gas per hour or more for 10 amps sucks.
A 24v alternator strapped to a 3hp predator engine can do better than that, a lot better.
|
I'm following all that logic, but I'm suggesting a compromise that is versatile in the extremes of powering a house, and a more minimal camping application that supplies lighting and cell phone charging.
12v has the versatility advantage, not efficiency.
I might build this just as a proof or denial of concept because I don't see any info. It would set me back $260 or less, and I'd have an awesome inverter at the end of the day.
|
|
|
02-05-2023, 12:58 PM
|
#8 (permalink)
|
Corporate imperialist
Join Date: Jul 2011
Location: NewMexico (USA)
Posts: 11,266
Thanks: 273
Thanked 3,569 Times in 2,833 Posts
|
A good 24v inverter will cost more than that.
__________________
1984 chevy suburban, custom made 6.5L diesel turbocharged with a Garrett T76 and Holset HE351VE, 22:1 compression 13psi of intercooled boost.
1989 firebird mostly stock. Aside from the 6-speed manual trans, corvette gen 5 front brakes, 1LE drive shaft, 4th Gen disc brake fbody rear end.
2011 leaf SL, white, portable 240v CHAdeMO, trailer hitch, new batt as of 2014.
|
|
|
02-05-2023, 01:12 PM
|
#9 (permalink)
|
lurker's apprentice
Join Date: May 2008
Location: the Perimeter
Posts: 942
PlainJane - '12 Toyota Tacoma Base 4WD Access Cab 90 day: 20.98 mpg (US)
Thanks: 504
Thanked 226 Times in 173 Posts
|
Do you have a well? I sized our original backup generator to handle the surge current needed to start our 240V well pump. I'd turn off the rest of the 240V stuff when we were on generator. It was adequate, but the lights would dim when the well pump kicked on and the microwave was distinctly weird sounding when it was consuming generator juice.
We've since installed a whole house unit because we added an outbuilding and the old generator just couldn't cope anymore.
|
|
|
02-05-2023, 03:26 PM
|
#10 (permalink)
|
Human Environmentalist
Join Date: Aug 2010
Location: Oregon
Posts: 12,754
Thanks: 4,316
Thanked 4,472 Times in 3,437 Posts
|
Quote:
Originally Posted by wdb
Do you have a well? I sized our original backup generator to handle the surge current needed to start our 240V well pump. I'd turn off the rest of the 240V stuff when we were on generator. It was adequate, but the lights would dim when the well pump kicked on and the microwave was distinctly weird sounding when it was consuming generator juice.
We've since installed a whole house unit because we added an outbuilding and the old generator just couldn't cope anymore.
|
City water, no well.
Only 240v appliance I run is the oven. Range is gas. AC is only run 2 months of the year, so it's normally off.
|
|
|
|